Welcome!
This community is for professionals and enthusiasts of our products and services.
Share and discuss the best content and new marketing ideas, build your professional profile and become a better marketer together.
CO2 Room programming
Version: 1.2
Theme: Functions Programming the SGC
on 7/31/23, 3:27 PM • 2,035 views
Hi People,
Last year I managed to control the CO2 in the room with the following configuration
But I must have made some changes that it is not working this year... :(
The idea is the CO2 socket will be ON for 5 minutes, stop, wait 2min30sec and turn on again if the conditions below prevail.
Light sensor must be above 65%, the Temp sensor below 29C and the CO2 sensor Below 1200ppm.
Why its not working, what am I missing?
Hope some guru of the forum will help me, please.
Regards,
Roberto
I don't like the CO2 Hyst of only 1ppm set this little more like 50ppm to not flip.
The mistake is you using a Impuls timer and bring the CO2 signal where usually goes Day/Night in ?
Make the Impuls timer correct with day night signal only and connect it with another and Function with the real dosing signal
Your Answer
Please try to give a substantial answer. If you wanted to comment on the question or answer, just use the commenting tool. Please remember that you can always revise your answers - no need to answer the same question twice. Also, please don't forget to vote - it really helps to select the best questions and answers!
About This Community
Themes
Question tools
Stats
Asked: 7/31/23, 3:27 PM |
Seen: 2035 times |
Last updated: 8/3/23, 6:37 AM |